What qualification does NFPA 72 list as acceptable for persons who prepare fire alarm system plans and specifications?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1061
- A: Certification by a nationally recognized fire alarm certification organization acceptable to the AHJ
Explanation
NFPA 72 lists qualified designers as those registered or licensed by a state or local authority, those certified by a nationally recognized fire alarm certification organization acceptable to the AHJ, or those factory trained and certified by the manufacturer. NICET certification is the common example of the second category.
More questions: Installation
- 1062Who must be able to show evidence of their qualifications to the AHJ on a fire alarm project?
- 1063Under the IBC, what is the maximum floor area of a single fire alarm zone in a building that requires zoning?
- 1064How does NFPA 70 require fire alarm circuits to be identified in the field?
- 1065A technician has looped an unbroken conductor under the terminal screw of each detector base on a Class B initiating circuit. Why is this a problem?
- 1066A technician suggests adding a T-tap from the middle of a conventional notification appliance circuit that ends in an end-of-line resistor. Why should you reject this?
- 1067To which UL standard must a fire alarm control unit be listed?