Question 1062 of 297 · NICET Fire Alarm Systems Level III
Who must be able to show evidence of their qualifications to the AHJ on a fire alarm project?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1062
- C: System designers, installers, and service personnel, when the AHJ asks
Explanation
NFPA 72 sets qualification requirements for designers, installers, and inspection, testing and maintenance personnel and requires evidence of qualification to be provided to the AHJ on request. A Level III supervisor should keep certificates for the crew available.
More questions: Installation
- 1063Under the IBC, what is the maximum floor area of a single fire alarm zone in a building that requires zoning?
- 1064How does NFPA 70 require fire alarm circuits to be identified in the field?
- 1065A technician has looped an unbroken conductor under the terminal screw of each detector base on a Class B initiating circuit. Why is this a problem?
- 1066A technician suggests adding a T-tap from the middle of a conventional notification appliance circuit that ends in an end-of-line resistor. Why should you reject this?
- 1067To which UL standard must a fire alarm control unit be listed?
- 1068A submittal for duct smoke detectors lists only a UL 268 listing. Which listing should you ask for instead?