Question 1063 of 297 · NICET Fire Alarm Systems Level III
Under the IBC, what is the maximum floor area of a single fire alarm zone in a building that requires zoning?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1063
- D: 22,500 sq ft, with each floor zoned separately
Explanation
The IBC requires each floor to be zoned separately and limits a zone to 22,500 sq ft and a length of 300 ft in any direction. Zoning lets responders go to the right area quickly, even on addressable systems that report individual points.
More questions: Installation
- 1064How does NFPA 70 require fire alarm circuits to be identified in the field?
- 1065A technician has looped an unbroken conductor under the terminal screw of each detector base on a Class B initiating circuit. Why is this a problem?
- 1066A technician suggests adding a T-tap from the middle of a conventional notification appliance circuit that ends in an end-of-line resistor. Why should you reject this?
- 1067To which UL standard must a fire alarm control unit be listed?
- 1068A submittal for duct smoke detectors lists only a UL 268 listing. Which listing should you ask for instead?
- 1069Where are the installation requirements for carbon monoxide detection in a commercial building located for current NFPA 72 projects?