Question 1064 of 297 · NICET Fire Alarm Systems Level III
How does NFPA 70 require fire alarm circuits to be identified in the field?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1064
- B: At terminal and junction locations, to prevent unintentional signals during testing and service
Explanation
Article 760 requires fire alarm circuits to be identified at terminal and junction locations. The purpose is to keep other trades and technicians from accidentally causing alarms or damage while working in shared boxes and terminal cabinets.
More questions: Installation
- 1065A technician has looped an unbroken conductor under the terminal screw of each detector base on a Class B initiating circuit. Why is this a problem?
- 1066A technician suggests adding a T-tap from the middle of a conventional notification appliance circuit that ends in an end-of-line resistor. Why should you reject this?
- 1067To which UL standard must a fire alarm control unit be listed?
- 1068A submittal for duct smoke detectors lists only a UL 268 listing. Which listing should you ask for instead?
- 1069Where are the installation requirements for carbon monoxide detection in a commercial building located for current NFPA 72 projects?
- 1070Which NFPA standard covers integrated testing of fire protection and life safety systems that interact with each other?