Question 1065 of 297 · NICET Fire Alarm Systems Level III

A technician has looped an unbroken conductor under the terminal screw of each detector base on a Class B initiating circuit. Why is this a problem?

Exactly one answer is correct.

Show solution

Correct answer to question 1065

  • A: Removing a detector would not open the circuit, so the trouble signal would not be generated

Explanation

Supervision depends on the circuit opening when a device or wire is removed. If the conductor is looped under the terminal without being cut, removing the device leaves the circuit intact and no trouble is reported, so the conductor must be broken at each connection point.

Next to question ›