Question 1065 of 297 · NICET Fire Alarm Systems Level III
A technician has looped an unbroken conductor under the terminal screw of each detector base on a Class B initiating circuit. Why is this a problem?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1065
- A: Removing a detector would not open the circuit, so the trouble signal would not be generated
Explanation
Supervision depends on the circuit opening when a device or wire is removed. If the conductor is looped under the terminal without being cut, removing the device leaves the circuit intact and no trouble is reported, so the conductor must be broken at each connection point.
More questions: Installation
- 1066A technician suggests adding a T-tap from the middle of a conventional notification appliance circuit that ends in an end-of-line resistor. Why should you reject this?
- 1067To which UL standard must a fire alarm control unit be listed?
- 1068A submittal for duct smoke detectors lists only a UL 268 listing. Which listing should you ask for instead?
- 1069Where are the installation requirements for carbon monoxide detection in a commercial building located for current NFPA 72 projects?
- 1070Which NFPA standard covers integrated testing of fire protection and life safety systems that interact with each other?
- 1071Your crew must connect new devices to an existing system in an occupied hospital, which will take the system out of service for part of a shift. What should happen first?