Question 1066 of 297 · NICET Fire Alarm Systems Level III
A technician suggests adding a T-tap from the middle of a conventional notification appliance circuit that ends in an end-of-line resistor. Why should you reject this?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1066
- C: The tapped branch would not be supervised, so a break there would go undetected
Explanation
On a conventional circuit, supervision current flows only through the path to the end-of-line device. A T-tap creates a branch that is not in that path, so an open on the branch is never seen. Addressable signaling line circuits may allow T-taps only where the manufacturer and the pathway class permit.