Why should a Level III verify the listing of every substituted device before it is installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1080
- D: Unlisted or incompatible substitutions can void the system listing and fail acceptance
Explanation
NFPA 72 requires equipment to be listed for its purpose, and many devices must be listed as compatible with the specific control unit. A substitution that is not compatible can fail to operate and will not match the approved submittal, so it has to be reviewed and approved first.