Which of the following is the best way to deal with a scope gap discovered mid-project, where the contract drawings show no detection in a new IT room that the code requires?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1079
- B: Notify the engineer or owner in writing and request direction or a change order before adding work
Explanation
Code compliance problems in the design need to be raised formally so the responsible design professional and owner can decide, and so cost and schedule impacts are handled through a change order. Quietly adding or ignoring work creates both code and contract problems.
More questions: Installation
- 1080Why should a Level III verify the listing of every substituted device before it is installed?
- 1081During rough-in inspection on a new office building, you find several fire alarm junction boxes above a hard lid ceiling with no access panel. What is the main concern?
- 1082A fire alarm interface relay will release the hold-open power for corridor smoke doors. How should the release be wired so it is fail-safe?
- 1083On a project where the AHJ requires a fire watch during the cutover from the old system to the new one, who is normally responsible for providing it?
- 1084A technician sets the panel to bypass the entire third floor while the ceiling contractor works there. Which control does the Level III need to ensure?
- 1085Which situation requires the installing contractor to perform reacceptance testing?