Question 2007 of 297 · NICET Fire Alarm Systems Level III

A building has fixed-temperature, nonrestorable spot heat detectors that were installed 15 years ago. What does NFPA 72 require at this point?

Exactly one answer is correct.

Show solution

Correct answer to question 2007

  • D: Replace them, or send 2 per 100 for laboratory testing

Explanation

Nonrestorable fixed-temperature detectors cannot be field tested with heat without destroying them. After 15 years they must be replaced or a sample of 2 detectors per 100 sent for laboratory testing; a failure in the sample requires further testing, and testing repeats at 5-year intervals.

Next to question ›