A building has fixed-temperature, nonrestorable spot heat detectors that were installed 15 years ago. What does NFPA 72 require at this point?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2007
- D: Replace them, or send 2 per 100 for laboratory testing
Explanation
Nonrestorable fixed-temperature detectors cannot be field tested with heat without destroying them. After 15 years they must be replaced or a sample of 2 detectors per 100 sent for laboratory testing; a failure in the sample requires further testing, and testing repeats at 5-year intervals.