Question 2006 of 297 · NICET Fire Alarm Systems Level III
During annual testing, how should a restorable spot-type heat detector be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2006
- A: With a heat source the manufacturer recommends, without damaging it
Explanation
Restorable heat detectors are tested with a heat source as recommended by the manufacturer, such as a listed heat gun, taking care not to damage the device. Open flames can scorch the unit and are not a recognized test method.
More questions: Maintenance
- 2007A building has fixed-temperature, nonrestorable spot heat detectors that were installed 15 years ago. What does NFPA 72 require at this point?
- 2008How is a nonrestorable line-type heat detector checked during periodic testing?
- 2009How often must manual fire alarm boxes be functionally tested?
- 2010Which test frequency does NFPA 72 assign to mechanical (vane) and pressure-type waterflow alarm devices?
- 2011Under NFPA 25, how often must sprinkler control valve supervisory switches be tested?
- 2012How often must audible and visible notification appliances be functionally tested?