A client asks why a semiannual waterflow test produced a signal at the central station 75 seconds after the inspector's test valve was opened. Does this meet the requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2090
- C: Yes, the alarm must occur within 90 seconds of flow
Explanation
Waterflow alarm devices must initiate an alarm within 90 seconds of flow equal to a single sprinkler. A 75 second response meets that limit, but a large retard setting should be reviewed if signals approach it.