Question 2090 of 297 · NICET Fire Alarm Systems Level III

A client asks why a semiannual waterflow test produced a signal at the central station 75 seconds after the inspector's test valve was opened. Does this meet the requirement?

Exactly one answer is correct.

Show solution

Correct answer to question 2090

  • C: Yes, the alarm must occur within 90 seconds of flow

Explanation

Waterflow alarm devices must initiate an alarm within 90 seconds of flow equal to a single sprinkler. A 75 second response meets that limit, but a large retard setting should be reviewed if signals approach it.