Question 2088 of 297 · NICET Fire Alarm Systems Level III
Which measurement is typically used when sound pressure levels are verified after a renovation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2088
- B: A-weighted readings in dBA, compared with ambient
Explanation
Audibility requirements are expressed in A-weighted decibels, which reflect how the human ear perceives sound. The measured alarm level is compared with the average ambient level and the maximum sound level lasting 60 seconds.
More questions: Maintenance
- 2089An ITM contract requires a quarterly visual inspection of a central station signaling path that the code requires only annually. Which frequency applies to the service company?
- 2090A client asks why a semiannual waterflow test produced a signal at the central station 75 seconds after the inspector's test valve was opened. Does this meet the requirement?
- 2001A new system with 400 spot smoke detectors was accepted last month. When must the first sensitivity test of those detectors be performed?
- 2002Your service team has completed the first two required sensitivity tests on a building's smoke detectors and every detector was within its listed range both times. What may the ITM manager do?
- 2003Which method does NOT measure smoke detector sensitivity and therefore cannot be used to satisfy the sensitivity test requirement?
- 2004A sensitivity report shows 12 detectors outside their listed sensitivity range. What does NFPA 72 require for those detectors?