Question 2089 of 297 · NICET Fire Alarm Systems Level III
An ITM contract requires a quarterly visual inspection of a central station signaling path that the code requires only annually. Which frequency applies to the service company?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2089
- B: The contract frequency, as it exceeds the code minimum
Explanation
NFPA 72 sets minimum frequencies. A contract may require more frequent work, and the service company is bound by its contract in addition to the code.