A new system with 400 spot smoke detectors was accepted last month. When must the first sensitivity test of those detectors be performed?

Exactly one answer is correct.

Show solution

Correct answer to question 2001

  • D: Within 1 year after installation

Explanation

NFPA 72 requires smoke detector sensitivity to be checked within 1 year after installation and then every alternate year. The early first check catches detectors that drift after the building is occupied and the HVAC is running.