Question 2001 of 297 · NICET Fire Alarm Systems Level III
A new system with 400 spot smoke detectors was accepted last month. When must the first sensitivity test of those detectors be performed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2001
- D: Within 1 year after installation
Explanation
NFPA 72 requires smoke detector sensitivity to be checked within 1 year after installation and then every alternate year. The early first check catches detectors that drift after the building is occupied and the HVAC is running.
More questions: Maintenance
- 2002Your service team has completed the first two required sensitivity tests on a building's smoke detectors and every detector was within its listed range both times. What may the ITM manager do?
- 2003Which method does NOT measure smoke detector sensitivity and therefore cannot be used to satisfy the sensitivity test requirement?
- 2004A sensitivity report shows 12 detectors outside their listed sensitivity range. What does NFPA 72 require for those detectors?
- 2005How often must the functional test of system smoke detectors be performed?
- 2006During annual testing, how should a restorable spot-type heat detector be tested?
- 2007A building has fixed-temperature, nonrestorable spot heat detectors that were installed 15 years ago. What does NFPA 72 require at this point?