Under the IBC, a manual fire alarm system is required in a Group A occupancy when which threshold is met?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3036
- D: 300 or more occupants, or more than 100 above or below exit discharge
Explanation
IBC 907.2.1 requires a manual fire alarm system in Group A where the occupant load is 300 or more, or more than 100 persons above or below the lowest level of exit discharge. Group A with 1,000 or more occupants also needs voice evacuation.