Question 3039 of 297 · NICET Fire Alarm Systems Level III

Under the IBC, when does a Group M occupancy require a manual fire alarm system?

Exactly one answer is correct.

Show solution

Correct answer to question 3039

  • C: 500 or more, or more than 100 above or below exit discharge

Explanation

IBC 907.2.7 sets the Group M threshold at a combined occupant load of 500 or more, or more than 100 above or below the lowest level of exit discharge. Sprinklered buildings may omit manual boxes under listed conditions.

Next to question ›