Under the IBC, when does a Group M occupancy require a manual fire alarm system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3039
- C: 500 or more, or more than 100 above or below exit discharge
Explanation
IBC 907.2.7 sets the Group M threshold at a combined occupant load of 500 or more, or more than 100 above or below the lowest level of exit discharge. Sprinklered buildings may omit manual boxes under listed conditions.
More questions: Submittal Preparation and System Layout
- 3040Under the IBC, when is a manual fire alarm system required in a Group F occupancy?
- 3041Under NFPA 101, when is a fire alarm system required in a new business occupancy?
- 3042Under the IBC and IMC, smoke detectors in return air ducts of an HVAC unit are generally required above which airflow?
- 3043A plans reviewer asks for proof that two-wire smoke detectors will work with your selected control unit. What should you submit?
- 3044A speaker circuit has 22 speakers tapped at 1 W and 8 speakers tapped at 2 W. The design rule leaves 20 percent spare amplifier capacity. What minimum amplifier rating is needed?
- 3045A 24 V power supply has a 6 A output. Strobes on four circuits draw 1.4 A, 1.6 A, 1.2 A, and 1.5 A in alarm. Is the supply adequate?