Under the IBC, which condition triggers a fire alarm system in a Group R-2 apartment building?

Exactly one answer is correct.

Show solution

Correct answer to question 3038

  • D: Units 3 or more stories above exit discharge, or more than 16 units

Explanation

IBC 907.2.9.1 requires a manual fire alarm system in Group R-2 where units are located three or more stories above the lowest level of exit discharge, more than one story below, or where the building contains more than 16 dwelling units, with exceptions.