Under the IBC, which condition triggers a fire alarm system in a Group R-2 apartment building?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3038
- D: Units 3 or more stories above exit discharge, or more than 16 units
Explanation
IBC 907.2.9.1 requires a manual fire alarm system in Group R-2 where units are located three or more stories above the lowest level of exit discharge, more than one story below, or where the building contains more than 16 dwelling units, with exceptions.
More questions: Submittal Preparation and System Layout
- 3039Under the IBC, when does a Group M occupancy require a manual fire alarm system?
- 3040Under the IBC, when is a manual fire alarm system required in a Group F occupancy?
- 3041Under NFPA 101, when is a fire alarm system required in a new business occupancy?
- 3042Under the IBC and IMC, smoke detectors in return air ducts of an HVAC unit are generally required above which airflow?
- 3043A plans reviewer asks for proof that two-wire smoke detectors will work with your selected control unit. What should you submit?
- 3044A speaker circuit has 22 speakers tapped at 1 W and 8 speakers tapped at 2 W. The design rule leaves 20 percent spare amplifier capacity. What minimum amplifier rating is needed?