Question 3040 of 297 · NICET Fire Alarm Systems Level III
Under the IBC, when is a manual fire alarm system required in a Group F occupancy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3040
- A: Two or more stories and 500 or more above or below exit discharge
Explanation
IBC 907.2.4 requires a manual system in Group F where the building is two or more stories in height and has an occupant load of 500 or more above or below the lowest level of exit discharge, with a sprinkler exception.
More questions: Submittal Preparation and System Layout
- 3041Under NFPA 101, when is a fire alarm system required in a new business occupancy?
- 3042Under the IBC and IMC, smoke detectors in return air ducts of an HVAC unit are generally required above which airflow?
- 3043A plans reviewer asks for proof that two-wire smoke detectors will work with your selected control unit. What should you submit?
- 3044A speaker circuit has 22 speakers tapped at 1 W and 8 speakers tapped at 2 W. The design rule leaves 20 percent spare amplifier capacity. What minimum amplifier rating is needed?
- 3045A 24 V power supply has a 6 A output. Strobes on four circuits draw 1.4 A, 1.6 A, 1.2 A, and 1.5 A in alarm. Is the supply adequate?
- 3046Why must strobe current values be taken at the lowest operating voltage when sizing circuits?