A plans reviewer asks for proof that two-wire smoke detectors will work with your selected control unit. What should you submit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3043
- A: The manufacturer's compatibility listing for that detector and panel
Explanation
Two-wire detectors get power from the initiating circuit and must be listed as compatible with the specific control unit. The compatibility document from the manufacturer is the proof reviewers need.
More questions: Submittal Preparation and System Layout
- 3044A speaker circuit has 22 speakers tapped at 1 W and 8 speakers tapped at 2 W. The design rule leaves 20 percent spare amplifier capacity. What minimum amplifier rating is needed?
- 3045A 24 V power supply has a 6 A output. Strobes on four circuits draw 1.4 A, 1.6 A, 1.2 A, and 1.5 A in alarm. Is the supply adequate?
- 3046Why must strobe current values be taken at the lowest operating voltage when sizing circuits?
- 3047Where more than two visible appliances are in the field of view, what must the design provide?
- 3048A strobe is mounted on the ceiling of a 30 ft by 30 ft room with a 10 ft ceiling. Which table should be used to select its rating?
- 3049In sleeping rooms, what is the minimum visible appliance rating when the appliance is more than 24 in below the ceiling?