Which closeout item gives the owner the narrative description of the system, operator instructions and the procedures for routine maintenance and testing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1041
- C: The owner's manual and installation instructions
Explanation
NFPA 72 completion documentation includes an owner's manual covering the system description, operating instructions, maintenance and testing requirements and manufacturer instructions. Test records document results but do not explain how to operate the system.
More questions: Installation, Planning and Maintenance Management
- 1042A construction manager asks when the fire alarm contractor's warranty period normally starts. What is the most common contract answer?
- 1043At the acceptance test for a new voice evacuation system, the contractor should already have completed which step?
- 1044A cost report shows a job is 50 percent complete, with 62,000 dollars spent against a 110,000 dollar total cost budget. What is the projected cost at completion if the overrun rate continues?
- 1045Which business record should a fire alarm department manager review to compare the estimated and actual labor hours for each completed project?
- 1046A building owner asks why the fire alarm ITM contract must also cover the interface relays for door release and fan shutdown. What is the best explanation?
- 1047When a building has several interconnected fire protection systems and is a high-rise, how often does the IFC require integrated testing in accordance with NFPA 4?