Question 1061 of 243 · NICET Fire Alarm Systems Level IV
How often must speakers and other audible notification appliances be functionally tested in an ITM program?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1061
- C: Annually
Explanation
Table 14.4.3.2 lists audible and visible notification appliances for annual functional testing. Visible appliances, speakers and horns are all part of the annual test.
More questions: Installation, Planning and Maintenance Management
- 1062A smoke detector is located above a production line that can only be shut down safely during a planned plant outage. How does NFPA 72 treat testing of devices in such inaccessible areas?
- 1063An owner with a large campus wants to change some test frequencies based on documented device reliability. What does NFPA 72 allow?
- 1064A generator that complies with NFPA 110 is installed as the secondary supply for a fire alarm system. What battery capacity is still required at the control unit?
- 1065A senior PM includes 8 percent contingency in a project budget. What is the purpose of that line?
- 1066Your network shows two technicians needed in week 6 and seven in week 7 for the same project. What scheduling technique smooths these peaks within available float?
- 1067Which item should a fire alarm project manager order immediately after contract award because its lead time often controls the schedule?