Question 1062 of 243 · NICET Fire Alarm Systems Level IV

A smoke detector is located above a production line that can only be shut down safely during a planned plant outage. How does NFPA 72 treat testing of devices in such inaccessible areas?

Exactly one answer is correct.

Show solution

Correct answer to question 1062

  • D: They may be tested during AHJ approved shutdowns, at intervals of no more than 18 months

Explanation

Devices that cannot be safely reached during normal operation may be tested during scheduled shutdowns if approved by the AHJ. The extended interval is still limited to 18 months.

Next to question ›