A generator that complies with NFPA 110 is installed as the secondary supply for a fire alarm system. What battery capacity is still required at the control unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1064
- D: Batteries for at least 4 hours of operation
Explanation
Where an emergency generator serves as the secondary supply, NFPA 72 still requires storage batteries with at least 4 hours of capacity to bridge the generator start and possible failures. Without a generator, 24 hours of standby plus the alarm duration is needed.
More questions: Installation, Planning and Maintenance Management
- 1065A senior PM includes 8 percent contingency in a project budget. What is the purpose of that line?
- 1066Your network shows two technicians needed in week 6 and seven in week 7 for the same project. What scheduling technique smooths these peaks within available float?
- 1067Which item should a fire alarm project manager order immediately after contract award because its lead time often controls the schedule?
- 1068Before installing devices, why must the shop drawings for a new system normally be approved?
- 1069A fire alarm system must recall elevators, close smoke dampers, release doors and shut down air handlers. Which coordination tool should be agreed with the mechanical, elevator and door hardware trades early in the project?
- 1070A company is invited to bid a design build fire alarm upgrade. What is the most important step before preparing the price?