What is the maximum time permitted for alarm verification on a smoke detector circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3029
- A: 60 seconds
Explanation
Alarm verification may delay the alarm signal, but the retard, reset and restart period must not exceed 60 seconds. It is not permitted on all detector types and must not be combined with other delays.
More questions: System Layout and NFPA 72 Requirements