Within what time after an initiating device activates must the fire alarm control unit activate the alarm notification appliances?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3028
- B: 10 seconds
Explanation
NFPA 72 requires the alarm notification signals to activate within 10 seconds after the initiating device activates, unless a permitted feature such as positive alarm sequence or verification applies.