How does the NEC require fire alarm circuits to be identified?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1058
- B: At terminal and junction locations, to prevent unintended signals during other work
Explanation
The NEC requires fire alarm circuits to be identified at terminal and junction locations so people working on other systems do not cause unwanted signals. A red jacket is common and may be a local requirement, but it is not the NEC rule itself.