Where must equipment supplying power-limited fire alarm circuits be marked as such?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1059
- D: Durably and plainly visible at the terminations
Explanation
Equipment supplying PLFA circuits must be durably marked where plainly visible at terminations to show that the circuits are power limited. This tells others that the PLFA wiring rules apply.