A fire alarm cable passes through a fire-rated wall. What must be done at the penetration?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1064
- C: Firestop it with an approved method that keeps the fire rating
Explanation
Electrical penetrations through fire-resistance-rated walls, floors and ceilings must be firestopped with approved methods so the rating is not reduced. Insulation or plain caulk is not a tested firestop system.