Question 1062 of 299 · NICET Fire Alarm Systems Level I
How must exposed fire alarm cables be installed according to the NEC?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1062
- B: In a neat and workmanlike manner, supported by the building structure
Explanation
Fire alarm cable must be installed neatly and supported by the building structure so it is not damaged by normal building use. Cable on top of ceiling tiles, taped to conduit, or hung from ceiling grid wires is not acceptable.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1063May fire alarm cables be supported by the hanger wires of a suspended ceiling grid?
- 1064A fire alarm cable passes through a fire-rated wall. What must be done at the penetration?
- 1065During a renovation you find old fire alarm cable that is no longer connected and not tagged for future use. What does the NEC require?
- 1066Cable is installed through bored holes in wood studs. If the hole is closer than the required distance to the face of the stud, what protection is required?
- 1067What is the minimum size for single conductors used in non-power-limited fire alarm circuits?
- 1068A fire alarm cable must be installed in an underground conduit between two buildings. What must the cable be rated for?