An exposed PLFA cable is run near open power and lighting conductors. What minimum separation does the NEC require in other applications?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1061
- D: 2 in.
Explanation
Where no barrier or raceway separates them, PLFA conductors must be kept at least 2 in. (50 mm) from electric light, power, Class 1 and NPLFA conductors, unless one of the listed exceptions applies.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1062How must exposed fire alarm cables be installed according to the NEC?
- 1063May fire alarm cables be supported by the hanger wires of a suspended ceiling grid?
- 1064A fire alarm cable passes through a fire-rated wall. What must be done at the penetration?
- 1065During a renovation you find old fire alarm cable that is no longer connected and not tagged for future use. What does the NEC require?
- 1066Cable is installed through bored holes in wood studs. If the hole is closer than the required distance to the face of the stud, what protection is required?
- 1067What is the minimum size for single conductors used in non-power-limited fire alarm circuits?