May a power-limited fire alarm cable be pulled into the same raceway as 120 V lighting conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1060
- B: No, PLFA must be separated from light and power conductors
Explanation
PLFA circuit conductors may not be placed in any cable, raceway or enclosure with electric light, power, Class 1 or NPLFA conductors, except where separated by a barrier or under the specific exceptions. Mixing them risks putting line voltage onto fire alarm circuits.