What is the minimum size for single conductors used in non-power-limited fire alarm circuits?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1067
- D: 18 AWG
Explanation
NPLFA circuit conductors may be 18 AWG or 16 AWG copper, or larger sizes sized for the load. 26 AWG is the minimum for conductors inside PLFA multiconductor cable, not for NPLFA.