During a renovation you find old fire alarm cable that is no longer connected and not tagged for future use. What does the NEC require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1065
- A: The accessible portion must be removed
Explanation
The accessible portion of abandoned fire alarm cable must be removed. Cable kept for future use must be identified with a tag. This keeps fuel load and confusion in ceiling spaces down.