Question 1068 of 299 · NICET Fire Alarm Systems Level I

A fire alarm cable must be installed in an underground conduit between two buildings. What must the cable be rated for?

Exactly one answer is correct.

Show solution

Correct answer to question 1068

  • D: Wet locations

Explanation

The interior of an underground raceway is a wet location under the NEC, so the cable must be listed for wet locations. Plenum rating addresses smoke and flame spread, not moisture.

Next to question ›