Question 1068 of 299 · NICET Fire Alarm Systems Level I
A fire alarm cable must be installed in an underground conduit between two buildings. What must the cable be rated for?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1068
- D: Wet locations
Explanation
The interior of an underground raceway is a wet location under the NEC, so the cable must be listed for wet locations. Plenum rating addresses smoke and flame spread, not moisture.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1069The branch circuit that supplies a fire alarm control unit must be which of the following?
- 1070How must the disconnecting means of the fire alarm branch circuit be marked?
- 1071Where must the location of the fire alarm branch circuit overcurrent device be recorded?
- 1072May the branch circuit for a fire alarm control unit be protected by a ground-fault circuit interrupter (GFCI)?
- 1073More than two conductors are pulled into a conduit. What maximum percentage of the conduit cross section may they fill?
- 1074Between pull points, what is the maximum total of bends allowed in an EMT run?