Question 1066 of 299 · NICET Fire Alarm Systems Level I
Cable is installed through bored holes in wood studs. If the hole is closer than the required distance to the face of the stud, what protection is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1066
- A: A steel plate at least 1/16 in. thick over the hole
Explanation
Holes in wood framing should be at least 1 1/4 in. from the nearest edge. If they are closer, a steel plate at least 1/16 in. thick protects the cable from nails and screws driven into the stud.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1067What is the minimum size for single conductors used in non-power-limited fire alarm circuits?
- 1068A fire alarm cable must be installed in an underground conduit between two buildings. What must the cable be rated for?
- 1069The branch circuit that supplies a fire alarm control unit must be which of the following?
- 1070How must the disconnecting means of the fire alarm branch circuit be marked?
- 1071Where must the location of the fire alarm branch circuit overcurrent device be recorded?
- 1072May the branch circuit for a fire alarm control unit be protected by a ground-fault circuit interrupter (GFCI)?