A new ionization smoke alarm without an alarm silencing feature is planned in a home near the kitchen range. What does NFPA 72 say about this location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1138
- B: Ionization alarms should not be within 20 ft of a permanent cooking appliance
Explanation
Because ionization alarms react strongly to cooking particles, NFPA 72 keeps ionization alarms without a silencing feature at least 20 ft from permanent cooking appliances. With a silencing feature the distance is 10 ft, and photoelectric alarms may be closer.