How is a manual fire alarm box normally tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2073
- C: By operating it as intended and resetting it per the manufacturer
Explanation
Manual boxes are tested by operating the handle or lever and confirming the alarm at the panel, then resetting the box, usually with a key or tool.