Question 2072 of 299 · NICET Fire Alarm Systems Level I
What should happen when a duct smoke detector that controls air movement goes into alarm during a test?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2072
- D: The fan shuts down or the dampers operate as the sequence requires
Explanation
Duct detectors are used to stop smoke spreading through the HVAC system, so their activation shuts down fans or operates dampers per the design. The test confirms both the signal and the control function.
More questions: Maintenance (Periodic Testing, Repair and Replacement)