Spot-type heat detectors on a smooth ceiling must be located so that all points on the ceiling are within what distance of a detector?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2021
- D: 0.7 times the listed spacing
Explanation
Every point on the ceiling must be within 0.7 times the listed spacing of a heat detector. Detectors must also be within one-half the listed spacing of walls.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2022A heat detector has a listed spacing of 50 ft. On a smooth flat ceiling, the maximum distance from the detector to a wall is
- 2023Spot-type heat detectors mounted on a sidewall must be located
- 2024For ceilings higher than 10 feet, the listed spacing of spot-type heat detectors must be
- 2025NFPA 72 guidance on placing spot-type smoke detectors says to keep them out of direct airflow and at least how far from an air supply diffuser or return opening?
- 2026Duct smoke detectors used for HVAC control
- 2027Under the adopted NFPA 90A, smoke detectors in the supply air system are required downstream of filters and ahead of branch connections in air distribution systems over