Pathway survivability Level 2 is generally provided by
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2039
- B: 2-hour rated cable or a 2-hour rated enclosure
Explanation
Level 2 survivability uses 2-hour fire resistive cables or systems, or a 2-hour rated enclosure or protected area. Level 3 adds full sprinkler protection.