A Class B initiating device circuit with a single open conductor will
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2038
- A: lose devices beyond the open and report a trouble
Explanation
A Class B pathway has no redundant path, so devices beyond the break cannot report. Supervision through the end-of-line device detects the open and indicates a trouble.