Question 2041 of 172 · Texas Fire Alarm License Exam
Sprinkler waterflow alarm-initiating devices must initiate an alarm signal within how long after flow equal to a single sprinkler of the smallest orifice?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2041
- D: 90 seconds
Explanation
Waterflow alarm-initiating devices must signal within 90 seconds of a flow equal to one sprinkler of the smallest orifice size in the system.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2042Heat detectors used to initiate elevator shunt trip must be located
- 2043A central station must retransmit a fire alarm signal to the communications center within
- 2044Under NFPA 70 Article 760, the branch circuit disconnecting means for fire alarm equipment must be
- 2045Which cable type is required for power-limited fire alarm circuits installed in a plenum without a raceway?
- 2046Power-limited fire alarm circuit conductors may NOT be placed in the same raceway with
- 2047How often are restorable spot-type heat detectors functionally tested after acceptance?