Question 2042 of 172 · Texas Fire Alarm License Exam
Heat detectors used to initiate elevator shunt trip must be located
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2042
- A: within 2 feet of each sprinkler and have a lower temperature rating
Explanation
Shunt trip heat detectors must be within 2 ft of each sprinkler and have a lower temperature rating and higher sensitivity than the sprinkler, so power is removed before water flows.