Question 2059 of 172 · Texas Fire Alarm License Exam
A double-action manual fire alarm box requires the user to
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2059
- B: perform two steps to initiate an alarm
Explanation
A double-action box needs two operations, such as lifting a cover or pushing in before pulling down, to reduce accidental activation.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2060A single open in a Class B notification appliance circuit causes
- 2061A conventional (non-addressable) initiating device circuit in normal condition reads a wire-to-wire short at the panel as
- 2062A wire-to-wire short on a supervised notification appliance circuit normally causes
- 2063Polarized notification appliances on a supervised NAC allow the control unit to
- 2064A panel shows a ground fault trouble. A common first step to locate it is to
- 2065With an IDC disconnected from the panel, an ohmmeter across the loop reads infinite resistance. This indicates