Question 2061 of 172 · Texas Fire Alarm License Exam
A conventional (non-addressable) initiating device circuit in normal condition reads a wire-to-wire short at the panel as
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2061
- D: an alarm
Explanation
Contact devices on a conventional IDC alarm by shorting the circuit through a low resistance, so a wire-to-wire short looks the same as an operated device.