Question 2060 of 172 · Texas Fire Alarm License Exam
A single open in a Class B notification appliance circuit causes
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2060
- C: a trouble signal, and appliances past the break will not sound
Explanation
The end-of-line device lets the control unit supervise the NAC. An open stops supervision current, causing a trouble, and the appliances beyond the open are lost.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2061A conventional (non-addressable) initiating device circuit in normal condition reads a wire-to-wire short at the panel as
- 2062A wire-to-wire short on a supervised notification appliance circuit normally causes
- 2063Polarized notification appliances on a supervised NAC allow the control unit to
- 2064A panel shows a ground fault trouble. A common first step to locate it is to
- 2065With an IDC disconnected from the panel, an ohmmeter across the loop reads infinite resistance. This indicates
- 2066Disconnected from the panel, a healthy Class B IDC with a 4.7 kilohm EOL resistor should read approximately