Article 760 requires exposed fire alarm cables to be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2069
- D: supported by the building structure so normal use will not damage them
Explanation
Fire alarm cables must be supported by the building structure and installed so that normal building use does not damage them. Ceiling tiles and sprinkler pipe are not supports.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2070The branch circuit supplying fire alarm equipment must NOT be
- 2071For NPLFA circuits, 18 AWG conductors must have overcurrent protection not exceeding
- 2072The minimum conductor size permitted for non-power-limited fire alarm circuits in a multiconductor cable is
- 2073When fire alarm cables pass through a fire-rated wall, the penetration must be
- 2074Circuit integrity (CI) cable is designed to
- 2075During an acceptance test of a new fire alarm system, the share of devices and circuits that must be tested is