Question 1043 of 344 · NICET Fire Alarm Systems Level II
Which mechanical protection is required for the fire alarm branch circuit disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1043
- B: Access limited to authorized personnel
Explanation
The circuit disconnecting means must be accessible only to authorized personnel, for example with a breaker lock, so the fire alarm supply cannot be turned off casually.
More questions: Installation
- 1044Where can conductors of a Class A NAC be allowed to share a single conduit for the outgoing and return run without violating the separation rule?
- 1045Where must a smoke detector used for elevator recall be located?
- 1046Which kind of detector is normally used to initiate elevator power shutdown (shunt trip) before sprinklers discharge in the machine room?
- 1047For elevator shunt trip, how close must the heat detector be to each sprinkler head it protects?
- 1048Which signal should a sprinkler waterflow switch with retard delay produce, and what is the maximum delay allowed before the alarm is initiated?
- 1049What is the nominal spacing for spot-type smoke detectors on a smooth ceiling when no other spacing is specified?