Question 1098 of 344 · NICET Fire Alarm Systems Level II
In a corridor not more than 20 ft wide, how far apart may visible appliances be spaced under the corridor rule of NFPA 72 (2022)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1098
- B: Not more than 100 ft apart and within 15 ft of each end
Explanation
The 2022 corridor rule allows 15 cd appliances within 15 ft of each end and no more than 100 ft apart. The 2025 edition removed this separate corridor paragraph, so corridors are then laid out with the general room tables. Check the edition you are tested on.