Question 1098 of 344 · NICET Fire Alarm Systems Level II

In a corridor not more than 20 ft wide, how far apart may visible appliances be spaced under the corridor rule of NFPA 72 (2022)?

Exactly one answer is correct.

Show solution

Correct answer to question 1098

  • B: Not more than 100 ft apart and within 15 ft of each end

Explanation

The 2022 corridor rule allows 15 cd appliances within 15 ft of each end and no more than 100 ft apart. The 2025 edition removed this separate corridor paragraph, so corridors are then laid out with the general room tables. Check the edition you are tested on.

Next to question ›