What is the correct way to functionally test a restorable heat detector?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2026
- D: Apply a heat source as the manufacturer directs
Explanation
Restorable heat detectors are tested with a heat source such as a listed heat gun, following the manufacturer's recommendations so the detector is not damaged. Shorting terminals only tests the circuit, not the detector.
More questions: Maintenance
- 2027A technician bypasses a zone for testing and forgets to restore it. What risk does this create?
- 2028The control unit shows a ground fault trouble. What is the most efficient first step to locate it?
- 2029A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?
- 2032A 24 VDC NAC with a 2.2 kilohm EOL is checked with the panel in normal (supervisory) condition. Which measurement confirms the EOL is in place?